Problem with new 20-amp dedicated circuits using PS Audio Power Port Premier Receptacles
Moose68Bash
Moose68Bash Posts: 3,843
edited September 2015 in Troubleshooting
On Wednesday I had an electrician in whom I have great confidence install two new dedicated 20-amp circuits for use with Perreaux mono blocks when I move them to a new location in my exercise-area system. Both circuits originate from the main panel for the house.
To test them, I plugged in the amp that I am now using in the exercise area. In each of the new circuits this produced a fairly loud hum from the amp.
At the same time, I also had the electrician install another new dedicated 20-amp circuit for use with a treadmill in the exercise area. This circuit uses a normal 20-amp GFCI receptacle, and unlike the PS Audio receptacles, it does not have an isolated ground.
When I tested the amp by plugging it into this new GFCI circuit, there was no hum. There is also no hum in the dedicated GFCI circuit I have been using for years for this amp in the exercise area. This circuit is wired into the same panel as the new circuits.
This suggests to me that something about the isolated-ground receptacles -- the PS Audio ones -- causes this hum, and as a test, I am thinking about replacing one of the PS Audio receptacles with a standard 20-amp GFCI receptacle to see whether this eliminates the hum.
However, before I do this, I would appreciate any thoughts others might have about this problem. The two new circuits are unusable for audio equipment in their present state.
Post edited by Moose68Bash on
    F1nut Posts: 50,815
    Not sure Phil, I use them all over and have never had that issue. Have the electrician come back out to have a look.
  • @F1nut,
    Thanks, Jesse.
    In the end, I'll probably have to have him come back, but I thought I'd try some simple diagnostics before he returns.
    As good as most electricians are, few of them in my experience have dealt with the peculiarities of audio set-ups.
    This electrician typically deals with commercial sites -- e.g., medical and dental facilities -- which often use hospital grade receptacles and isolated-ground receptacles for sensitive equipment. I hope he can figure it out.
    F1nut Posts: 50,815
    What gauge and type of wire did he run? Are the two new lines grounded on the same leg or opposite legs in the breaker box?
  • BlueFox
    BlueFox Posts: 15,251
    I would suggest Shunyata for power. From my experience, their technology works fantastic.
    F1nut Posts: 50,815
    Bud, your comment is out of place. It doesn't matter if he uses a PS Audio, Shunyata or generic hospital grade receptacle as the technology is exactly the same, they all have isolated grounds.
  • Just curious......why the GFCI's?
    Modwright SWL 9.0 SE (6Sons Audio Thunderbird PC with Oyaide 004 terminations)
    Consonance cd120T
    Consonance Cyber 800 tube monoblocks (6Sons Audio Thunderbird PC's with Oyaide 004 terminations)
    Usher CP 6311
    Phillips Pronto TS1000 Universal Remote
  • mantis
    mantis Posts: 17,206
    It sounds like your on a circuit with other motors possibly. That would cause the hum.
    Another thing that causes hum's is poor grounded Cable systems. Depending not eh circuit again which they live on.
    This also goes with DSS , the Dish could have a poor ground causing the Polarity difference to cause the hum.
    Hum's are pretty easy to fix and find. What is strange is the fact that you said they are dedicated circuits. Dedicated circuits usually don't cause any hum unless possibly the breaker is faulty or a poor ground at the panel for that or those circuits.
    I would absolutely get the Electrician back involved to isolate the issue.
    PS audio outlets I also have been using for years with no issues. I have a dedicated true 20 amp circuit at my head end or gear location and I have no hums.
    Dan
  • Moose68Bash
    Thanks, guys, for your interest and advice.
    Let me start with Jesse's questions:
    I used the same electrician and a PS Audio Power Port Premier receptacle in installing the dedicated circuit to my main system, and it has functioned perfectly. I don't think it's the PS Audio product per se. I suspect it is something about this particular configuration/installation.
    The wire is the same wire used in the dedicated circuit to my main rig -- that is, 12 AWG Romex with four conductors, hot, neutral, and two insulated ground wires. It is manufactured by Southwick Wire.
    The two new circuits are wired to my main service panel which is only a few feet from the receptacles themselves.
    These two new circuits are wired to the same leg of the breaker box, as are the three additional dedicated circuits in the exercise area of the basement, where my rig is located.
    These other three dedicated circuits provide power to:
    1. A surge protector into which the stereo equipment (not the amp) are plugged, along with the TV, cable box, and DVD player. The stereo equipment includes a preamp, PS Audio PW DAC MKII, a Wadia iPod dock connected to the DAC via coax, and a Cambridge Audio Azur 840C CD player that I use only as a CD transport to feed the DAC via optical connection. Yes this is a mess! And, it will be easy to eliminate potential sources of the problem from this mess.
    2. A power source for a Cybex Arc Trainer, that is plugged into the receptacle only while the machine is in use. The hum is present when the machine is not plugged in. This was supposed to be a fully dedicated circuit, but the installer of a stand-by generator tapped into it for the trickle charger for the battery in the generator because it happened to be located right next to the main panel.
    3. A power source for a Trotter treadmill, which like the Arc Trainer, is unplugged when not in use. The hum is present when the treadmill is not plugged in.
    My main panel brings in 200 A service, which it distributes not only to various specific appliances/equipment (A/C compressors, air handlers, condensation pumps; water softening equipment, kitchen circuits, etc.) but also to three subpanels (garage, attic air handler, laundry room).
    I think the main panel has 40 slots for breakers, some of which are coupled to allow for breakers for heavy-duty equipment (e.g., A/C compressors) and some of which have been set up with "slim" breakers so that one slot in the panel can accommodate two circuits. Each of the dedicated circuits falls into this last category -- that is, each is wired into the main panel using one of these "slim" breakers that allow two circuits into one slot.
    In New Hampshire, GFCI receptacles are required by code in any installation below grade, like my basement, unless the receptacle is a specialized circuit -- e.g., like an isolated ground circuit for sensitive equipment. {This is the explanation of my electrician.)
    mantis wrote: »
    There are several "motors" wired into this panel (see above). If one or more of these are the source of the hum, I've got bigger problems. I can probably shut down their breakers to see whether they are the source, but I'll do that after I check out sources that will have less draconian consequences for my wallet.
    I have suspected that the cable TV set up may be a source of the problem, and I'll check that out today. This is an easy one to eliminate.
    We've never had a grounding problem in the 18 years we've lived in this house, but I'm beginning to really push the capacity of the circuitry by adding more circuits and more equipment. However, the electrician told me that, although I keep adding "stuff," I'm still not getting close to the maximum capacity of the 200 A service we have.
    One question: Would it help to have a small subpanel installed, into which these fie dedicated circuits could be wired? Would that help isolate them from the heavy equipment wired into the main panel?
    Again, thank you all for your help and advice. You've certainly given me food for thought and some actions I can take.
    I'll do some homework that I can handle on my own, then I'm sure I'm going to have the electrician return, probably to do some reconfiguration of the wiring in the main panel, if possible.
    F1nut Posts: 50,815
    Right, that was my point to BlueFox.
    Yeah, that's not it either.
    I'm not 100% on this, but I would have run the two new lines on opposite legs.
  • Moose68Bash
    Perhaps, I should have watched the electrician while he was doing the installation to ensure he did wire the two on opposite legs.
    Inspired by your previous comments, however, I went down to the exercise area and went through a series of unplugging steps to try to identify whether a piece of equipment on my rack was the cause.
    Bingo!
    After having progressed through unplugging the cable box, cable connection, TV, DVD player, and CD player, when I unplugged the PS Audio PerfectWave DAC MKII, the hum disappeared.
    The DAC had been plugged into the surge protector that was plugged into the GFCI receptacle that pre-existed all these changes. Before these changes, the amp had also been plugged into this receptacle, albeit not through the surge protector. I had never had a hum.
    So, I left the amp plugged into one of the two new dedicated circuits with the PS Audio receptacles and then plugged the DAC into the other new dedicated circuit with a PS Audio receptacle.
    No hum.
    Then, I plugged the amp into the same receptacle as the DAC.
    No hum.
    Then, I plugged the DAC sequentially into each of the other GFCI receptacles.
    The hum reappeared in each instance.
    So, I have reached the end of what I can do.
    If I can plug the DAC into one of the two receptacles into which I shall eventually plug one of the mono blocks, and I don't get a hum (and based on the above "experiments," I don't expect to get a hum), then I can live with the status quo.
    But if this would be risky for either the DAC or the mono block with which the DAC shares a receptacle, or if this compromises sound quality, then I still have to do something about the configuration of the GFCI receptacles in relation to the two new dedicated "audio" circuits. Or, perhaps, I can just have another dedicated circuit installed for the DAC.
    Again, thanks Jesse, Blue Fox, Midnite Mick, and Mantis for your interest.
    Any additional comments about this will be greatly appreciated.
    F1nut Posts: 50,815
    I'm glad you were able to find the issue. What a relief, eh?
    I hate GFCI receptacles, nothing but trouble.
  • Midnightmick, you've seen them a thousand times.They are the the rectangle recepticles that have usually a red reset button on them and used near water sources like kitchens and bathrooms. Formal name Ground Fault Circuit Indicator. If a short or ground happens near that outlet it will automatically shut down so you don't get electrocuted like the scene in the James Bond flick where he throws the heater in the bath and fries the guy. They do serve a purpose and are code everywhere.
  • F1nut wrote: »
    Yes, Jesse, I'm very relieved, and I think I'll get a third dedicated circuit installed with an isolated ground receptacle.
    I had never realized that GFCI circuits were trouble, but I've and learn!
    Hello Leftwinger,
    I am familiar with GFCI's I was just questioning the purpose. Where I am from they are only required within 1.5 m of a water source. Different codes, hence the confusion. We generally only see them in Kitchen's, washrooms, laundry rooms, and exterior.
    Regards,
    Mike
    Consonance cd120T
    Usher CP 6311
  • Sorry.
    Glad you found your problem.
    Regards,
    Mike
    Consonance cd120T
    Usher CP 6311
  • @Midnite Mick,
    Thank you.
    Wouldn't it be nice if they were all that easy to find?
    Cheers! :)
  • In a typical wood framed home, a Romex® wired circuit does not required an Isolated Ground. An Isolated Ground may be effective if metal conduit (ridged or flexible), metal building framing or other conductive metal is involved.
    We should note that Isolated Grounds are often mis-wired and in commercial building with the passing of time become corrupted by newer electricians.
    In this thread's situation, the Safety Ground and the Isolated Ground should be connected to the same bus bar in the main circuit box.
  • @Speedskater,
    Thank you for that explanation of the way an isolated-ground receptacle should be wired to the bus bar in the main circuit box and other aspects of the use of isolated-ground receptacles.
    One question:
    At the receptacle end of the circuit, one of the two insulated ground wires goes to the green terminal screw on the receptacle and the other goes to the green screw in the receptacle box.
    Then, however, unlike the wiring for a standard receptacle, the grounding screw in the receptacle box is not connected with a pig-tail to the receptacle itself.
    Is that correct?
  • I don't have a dual IG receptacle handy to look at.
    But I would go with just connecting the IG to the receptacle. As the yoke is not connected to the working parts.
  • @Speedskater,
    Thank you.
    I think code requires connecting the second ground wire to the metal box the into which the receptacle fits.
  • Doesn't it have one of those automatic grounding spring tabs on the yoke?
  • No, not that I recall. It only has the green grounding screw, and the yoke is insulated from the receptacle, I understand the way an isolated ground receptacle is built.
  • The yoke has a brass spring section that:
    Automatic grounding system eliminates need for bonding jumper in metal enclosures
    or
    Solid one-piece brass mounting strap with integral ground contacts assures ground integrity
  • So the regular Safety Ground wire (Green) attaches to the metal outlet box. The receptacle yoke's ground contact connects to the metal outlet box.
    The IG wire (Green/Yellow) connects to the receptacle's isolated ground screw.
    The only one place that the Safety Ground and the IG connect together is in the breaker box.
    @Speedskater,
    I don't recall seeing any spring of any sort on the receptacle.
    I've ordered two more Power Port receptacles that should be here tomorrow. I'll take a look at those.
    I am not that familiar with the nomenclature for parts of receptacles, but here's what I found on the net:
    This looks exactly like the construction of the receptacles that my electrician installed. Basically, it seems, that the "brass mounting strap" is isolated from the "green grounding screw" and therefore from the grounding contacts. I think this is what differentiates an isolated ground receptacle from standard receptacles.
    I'm not clear about what you refer to as the 'yoke." Is that what they call the "brass mounting strap" in this diagram?
  • Yes the 'yoke' is "brass mounting strap".
    The silver clip under the top mounting screw is the grounding contact.
  • drumminman
    drumminman Posts: 3,396
    Moose, I've always read that you should have digital on a separate line or isolated from analog equipment as it tends to muddy up ac power. It would be worth experimenting with that in mind.
    @Speedskater,
    That's what I thought. The diagram below shows that the "yoke" in an isolated ground receptacle is insulated from the body of the receptacle ("insulated barrier construction" in the first diagram). I'm not sure what the "grounding contact" on an isolated ground receptacle actually does.
  • While it's real hard impossible to read the text in that drawing.
    I see an extra connection where the White and Green wires join. In fact the Green/Yellow should connect directly to the IS receptacle IS ground screw.
  • As for the digital on one circuit and the analog on another, that's just another AC power misunderstanding.
    Digital audio circuits operate in one frequency range and analog audio in another.
    Jim Brown writes that everything (save for big power amps) should be on one circuit where practicable.