    With that said, I have always wondered why 20 amps? I doubt the average rig doesn't pull anywhere near that even when cranked, so why not 15 amps?

    The NEC requires a 20% margin on the breaker, so while a 15 amp breaker is capable of 1800 watts the max draw is restricted to 1440 watts. You add up the potential max draw of your gear and if it exceeds 1440 watts you should use a 20 amp breaker along with at least 12 gauge wire. Even better, use 10 gauge.

    With your current 10 amp/1200 watt capable breaker the max draw would be restricted to 960 watts. If your current wire is at least 14 gauge you can simply change the breaker to a 15 amp and still meet code.
    Political Correctness'.........defined

    "A doctrine fostered by a delusional, illogical minority and rabidly promoted by an unscrupulous mainstream media, which holds forth the proposition that it is entirely possible to pick up a t-u-r-d by the clean end."


    President of Club Polk

  • disneyjoe7
    disneyjoe7 Posts: 11,435
    edited January 2014
    Agreed :smile: all of the above.

    Speakers
    Carver Amazing Fronts
    CS400i Center
    RT800i's Rears
    Sub Paradigm Servo 15

    Electronics
    Conrad Johnson PV-5 pre-amp
    Parasound Halo A23
    Pioneer 84TXSi AVR
    Pioneer 79Avi DVD
    Sony CX400 CD changer
    Panasonic 42-PX60U Plasma
    WMC Win7 32bit HD DVR


  • Glen B
    Glen B Posts: 269
    edited January 2014
    It is important to understand the correct implementation of household circuit breaker derating rules. Breakers are rated for 100% of their rating, but because of concerns about the effects of heat generation from continuous loads (i.e., loads that run uninterrupted for 3 or more hours) the NEC/NFPA requires 80% derating for such loads.

    Loads that are not continuous (i.e., run uninterrupted for less than 3 hours) are not subject to an 80% derating, and may be up to 100% of the breaker rating. Air conditioners, refrigerators, lighting, single appliances that draw at least 80 percent of the circuit capacity are considered continuous loads. Microwaves, toasters, most audio/video equipment, etc., are not considered continuous loads.

    Pure class A amplifiers that draw their maximum current continuously would be subject to the 80% rule if they draw 12A or 16A. Class AB and other classes that draw their maximum current on peaks, are not a continuous load. There may be exceptions, use common sense. I have power tools like my miter saw and air compressor that are rated at 15 running amps and run on a 15A circuit. These tools run for only seconds to a couple of minutes respectively and are not subject to the 80% rule.
    Main System: Denon DP-59L | Audio-Technica AT33EV | Marantz SA-11S2 | Classe DR-10 | Classe CA-300 | Classe RC-1 | PSB Stratus Gold i's | DIY Balanced AC Power Conditioner | Acoustic Zen and NeoTech cables | Oyaide and Furutech power connectors | Dedicated 20A isolated ground line.

    Home Theater: Toshiba D-VR5SU | Laptop #1 |Outlaw Audio OAW3 wireless audio system | Marantz SR-19 | Phase Linear 400 Series 2, modified | AudioSource 10.1 EQ (for subs) | Axiom M3 v3’s | Axiom VP150 | Optimus PRO-X55AVs | Dayton 12” powered subs (x2) | Belkin PureAV PF-60 line conditioner.

    Party System: Laptop #2 | Audioquest Dragonfly USB DAC | Technics SU-A6 | Acurus A-250 | Radio Shack 15-band EQ | Pioneer SR-9 reverb | Cerwin Vega DX9's | Dayton 100° x 60° horns with titanium HF/MF compression drivers.
  • Speedskater
    Speedskater Posts: 495
    edited January 2014
    "Glen" that's a very good explanation. There is so much confusion between 'continuous', 'maximum' and 'rated' currents.