Circuit Panel Capacity?

mufsoman
mufsoman Posts: 632
I'm thinking of adding some dedicated circuits for the HT setup. I currently have most of my equipment plugged in to one outlet on a shared circuit. Never had any issues with it even though the breaker is only 10 amps. However, I'm close to pulling the trigger on another amp, so I think its time.

I know there are formulas/rules of thumb for how many circuits/amps can be run off of one panel, so if I would be going over the limit, I'll pursue a second panel.

This current panel has 31 10 amp breakers and one 30 amp. Can I just added two 20 amp circuits to this existing panel? Thanks
Parasound HCA-2003A & 2205A
Front: Rti12's
Center: Csi A6
Side surrounds: Polk Rti A1's
Atmos: Mirage Nanosats
APC H15
Power cords by Pepster, Morrow MA4 IC's, AQ Midnight, AQ Chocolate HDMI's[/SIZE]
The rest is TBD.
Post edited by mufsoman on
«1

Comments

  • rpf65
    rpf65 Posts: 2,127
    edited January 2014
    Not an electrician, but have a limited working knowledge of electrical codes.

    You can add extra circuits as long as you have both a place on the power bar as well as a free lug for the neutral. You don't want to share neutral lugs with another circuit. You can share ground lugs, commonly called piggy backing, but not recommended for neutrals.

    There is a rule for adding a second, or more sub-panels, but none for individual breakers in a breaker box that I'm aware of.
  • GlennDog
    GlennDog Posts: 3,120
    edited January 2014
    That picture implies you have room for 7 more circuits. However, that is not always the case. There should be no problem. In that modern panel shown, there should be just as many spots on the neutral bus bar as there is for grounds on the ground bus bar, (meaning you don't want to share grounds, either.) I'm not an electrician either, but I've been around the block.
    AC Regenerator PS Audio PerfectWave Power Plant 10
    Source Lumin U1 Mini into Lampizator Baltic 4 DAC
    Pre Cary SLP-05
    Power Rogue M180 Dark monos
    Mains Salk HT2-TL
    Rythmik F12
  • Msabot1
    Msabot1 Posts: 2,098
    edited January 2014
    Should work ok..that is a modern panel..keep the grounds and neutrals dedicated to their own lugs...just like that was mentioned earlier.
  • disneyjoe7
    disneyjoe7 Posts: 11,435
    edited January 2014
    Not to derail here but.... 10 amp circuits never seen those before?

    Speakers
    Carver Amazing Fronts
    CS400i Center
    RT800i's Rears
    Sub Paradigm Servo 15

    Electronics
    Conrad Johnson PV-5 pre-amp
    Parasound Halo A23
    Pioneer 84TXSi AVR
    Pioneer 79Avi DVD
    Sony CX400 CD changer
    Panasonic 42-PX60U Plasma
    WMC Win7 32bit HD DVR


  • mufsoman
    mufsoman Posts: 632
    edited January 2014
    DJ7 - I thought it was odd to have all 10 amps circuits too, but apparently thats the way all the homes in our subdivision are wired. The 30 amp circuit is for the AC. The furnace, kitchen appliances, washer/dryer, are all on separate circuits, but obviously 10 amp each. There are a lot of circuits, so the house seems to be pretty well distributed. However, I'm not an electrician....
    Parasound HCA-2003A & 2205A
    Front: Rti12's
    Center: Csi A6
    Side surrounds: Polk Rti A1's
    Atmos: Mirage Nanosats
    APC H15
    Power cords by Pepster, Morrow MA4 IC's, AQ Midnight, AQ Chocolate HDMI's[/SIZE]
    The rest is TBD.
  • chumlie
    chumlie Posts: 8,658
    edited January 2014
    Forgot the English button spammer.
  • F1nut
    F1nut Posts: 50,647
    edited January 2014
    There should be no problem. In that modern panel shown, there should be just as many spots on the neutral bus bar as there is for grounds on the ground bus bar, (meaning you don't want to share grounds, either.)

    Aren't the ground and neutral bars one and the same with two bars total, one bar per side?
    Political Correctness'.........defined

    "A doctrine fostered by a delusional, illogical minority and rabidly promoted by an unscrupulous mainstream media, which holds forth the proposition that it is entirely possible to pick up a t-u-r-d by the clean end."


    President of Club Polk

  • Speedskater
    Speedskater Posts: 495
    edited January 2014
    While the Neutral bus bar and the Ground bus bar may be the same thing they often are very different animals. In a sub-panel they must be different.
  • Speedskater
    Speedskater Posts: 495
    edited January 2014
    A 100 Amp 'Circuit Panel' (Panel Board) could have thirty two 20 Amp breakers. So long as the total current at any given time though all 32 breakers sums to less than 100 Amps, you are good.
  • amulford
    amulford Posts: 5,020
    edited January 2014
    You will only need one circuit. I would go with a 15 amp, if you go 20 be sure to run at least 12 Ga wire.

    I would avoid two because of a possible ground loop issue. With only one ground you cut down on the possibility somewhat.

    you have plenty of space in the panel.
  • F1nut
    F1nut Posts: 50,647
    edited January 2014
    While the Neutral bus bar and the Ground bus bar may be the same thing they often are very different animals. In a sub-panel they must be different.

    So, in some panels they are one and the same and in others they are individual? I can't say I've seen a panel with individual bars, but then again, I haven't seen them all.
    Political Correctness'.........defined

    "A doctrine fostered by a delusional, illogical minority and rabidly promoted by an unscrupulous mainstream media, which holds forth the proposition that it is entirely possible to pick up a t-u-r-d by the clean end."


    President of Club Polk

  • mufsoman
    mufsoman Posts: 632
    edited January 2014
    I live in the Chicago area, so everything is metal conduit with separately pulled wires. There is no ground wire. Outlets are "grounded" through contact with the metal conduit.

    So I will have 2 amps, 2 subs, AVR and the rest of the gear to plug in. I was planning on having one circuit for each amp and a third for all else. Three dedicated circuits total, either 15 or 20 amps each. Alternate recommendations???
    Parasound HCA-2003A & 2205A
    Front: Rti12's
    Center: Csi A6
    Side surrounds: Polk Rti A1's
    Atmos: Mirage Nanosats
    APC H15
    Power cords by Pepster, Morrow MA4 IC's, AQ Midnight, AQ Chocolate HDMI's[/SIZE]
    The rest is TBD.
  • pitdogg2
    pitdogg2 Posts: 25,563
    edited January 2014
    F1nut wrote: »
    So, in some panels they are one and the same and in others they are individual? I can't say I've seen a panel with individual bars, but then again, I haven't seen them all.

    No I'll clarify.

    In a sub panel like say a garage you must separate neutral and grounds IF the sub panel don't have it's own ground rod.
    Which means you have not tied the two together at the panel. There is a screw that ties both together you do not use that screw that way they are separate

    From what I was told by my electrician was that what COULD happen IF I did tie them together the ground at the garage COULD become the house ground going through too small of wire..ie PROBLEMS different ground potential's

    If the panel has its own ground rod they can be together as both go to the same as you are NOT using the house ground

    In my home panel ground and neutral are both connected to the same depending on placement L/R side of the panel

    For my garage project I had to buy an individual ground bar. That is why you have not seen one Jesse
  • nspindel
    nspindel Posts: 5,343
    edited January 2014
    While the Neutral bus bar and the Ground bus bar may be the same thing they often are very different animals. In a sub-panel they must be different.

    The man speaks the truth. When I installed a subpanel it was definitely code that the neutral and the ground had to be different.
    Good music, a good source, and good power can make SDA's sing. Tubes make them dance.
  • dkg999
    dkg999 Posts: 5,647
    edited January 2014
    I would check your ground at the end of each circuit. I rewired a house that used the metal conduit for the ground, and with corrosion on each of the connections, most of the circuits had problems with grounding.
    DKG999
    HT System: LSi9, LSiCx2, LSiFX, LSi7, SVS 20-39 PC+, B&K 507.s2 AVR, B&K Ref 125.2, Tripplite LCR-2400, Cambridge 650BD, Signal Cable PC/SC, BJC IC, Samsung 55" LED

    Music System: Magnepan 1.6QR, SVS SB12+, ARC pre, Parasound HCA1500 vertically bi-amped, Jolida CDP, Pro-Ject RM5.1SE TT, Pro-Ject TubeBox SE phono pre, SBT, PS Audio DLIII DAC
  • pitdogg2
    pitdogg2 Posts: 25,563
    edited January 2014
    dkg999 wrote: »
    I would check your ground at the end of each circuit. I rewired a house that used the metal conduit for the ground, and with corrosion on each of the connections, most of the circuits had problems with grounding.

    You will have that with steel.
  • Msabot1
    Msabot1 Posts: 2,098
    edited January 2014
    nspindel wrote: »
    The man speaks the truth. When I installed a subpanel it was definitely code that the neutral and the ground had to be different.

    Ground connections and neutral connections are two different animals in a breaker box my friend...they are not one in the same!
  • Speedskater
    Speedskater Posts: 495
    edited January 2014
    mufsoman wrote: »
    I live in the Chicago area, so everything is metal conduit with separately pulled wires. There is no ground wire. Outlets are "grounded" through contact with the metal conduit.
    [..............................]
    Yes, circuits are often grounded (EGC) using metal conduit (or EMT). This metal conduit will carry much more fault current than a wire. But it is often said that conduit can have long term problems from damage and bad connections.
  • leftwinger57
    leftwinger57 Posts: 2,917
    edited January 2014
    Before I would say yea go ahead and do it. I would first see what the breaker box is rated for and then what load your carrying now. Don't assume because you have a bunch of extra knock outs that you can just arbitrarily add circuits as you please. Yes 20amp breakers should work.If only using the new lines for your audio gear and nothing heavy like a generator or freezer. I certainly would ask a lineman or an electrician can this be done to be on the safe side. As far as I saw everyone here admitted they were not electricians and certainly can't know codes of every state.My complex is well over 50 years old has 15 amp breakers and used aluminum cable and metal boxes. I don't think Romex was even invented yet. Good luck on your project....
    2chl- Adcom GFA- 555-Onkyo P-3150v pre/amp- JVC-QL-A200 tt- Denon 1940 ci cdp- Adcom GFS-6 -Modded '87 SDA 2Bs - Dynamat Ext.- BH-5- X-Overs VR-3, RDO-194 tweeters, Larry's Rings, Speakon/Neutrik I/C- Cherry stain tops Advent Maestros,Ohm model E

    H/T- Toshiba au40" flat- Yamaha RX- V665 avr- YSD-11 Dock- I-Pod- Klipsch #400HD Speaker set-

    Bdrm- Nikko 6065 receiver- JBL -G-200s--Pioneer 305 headphones--Sony CE375-5 disc
  • F1nut
    F1nut Posts: 50,647
    edited January 2014
    pitdogg2 wrote: »
    In my home panel ground and neutral are both connected to the same depending on placement L/R side of the panel

    Right, that's what I was saying. Not sure where all this sub-panel talk came from, the OP never brought that up.
    Ground connections and neutral connections are two different animals in a breaker box my friend...they are not one in the same!

    They are terminated to the same bar.
    Political Correctness'.........defined

    "A doctrine fostered by a delusional, illogical minority and rabidly promoted by an unscrupulous mainstream media, which holds forth the proposition that it is entirely possible to pick up a t-u-r-d by the clean end."


    President of Club Polk

  • GlennDog
    GlennDog Posts: 3,120
    edited January 2014
    I certainly would ask a lineman or an electrician can this be done to be on the safe side. As far as I saw everyone here admitted they were not electricians and certainly can't know codes of every state.

    Exactly. Each AHJ (Authority Having Jurisdiction) has the end-all-be-all say so in the way buildings are constructed. 'Round here, detached structures like garages & out-buildings that have their own sub-panel have to have their own ground rod and the neutral wires inside the panel must "float" (meaning it must be separated from the metal panel board & the ground bus bar. Also, new construction requires 2 ground rods at the main structure. Bonding is enforced, as well i.e. above the water tank the gas line & the hot and cold pipes need to be bonded/connected thru approve connectors like a Weaver clamp with the appropriate gauge wire, 6 AWG in most cases
    AC Regenerator PS Audio PerfectWave Power Plant 10
    Source Lumin U1 Mini into Lampizator Baltic 4 DAC
    Pre Cary SLP-05
    Power Rogue M180 Dark monos
    Mains Salk HT2-TL
    Rythmik F12
  • Glen B
    Glen B Posts: 269
    edited January 2014
    dkg999 wrote: »
    I would check your ground at the end of each circuit. I rewired a house that used the metal conduit for the ground, and with corrosion on each of the connections, most of the circuits had problems with grounding.

    How old was the rewire work ? It takes a long time for corrosion to occur, unless the conduit is in a damp environment or close to the ocean.
    Main System: Denon DP-59L | Audio-Technica AT33EV | Marantz SA-11S2 | Classe DR-10 | Classe CA-300 | Classe RC-1 | PSB Stratus Gold i's | DIY Balanced AC Power Conditioner | Acoustic Zen and NeoTech cables | Oyaide and Furutech power connectors | Dedicated 20A isolated ground line.

    Home Theater: Toshiba D-VR5SU | Laptop #1 |Outlaw Audio OAW3 wireless audio system | Marantz SR-19 | Phase Linear 400 Series 2, modified | AudioSource 10.1 EQ (for subs) | Axiom M3 v3’s | Axiom VP150 | Optimus PRO-X55AVs | Dayton 12” powered subs (x2) | Belkin PureAV PF-60 line conditioner.

    Party System: Laptop #2 | Audioquest Dragonfly USB DAC | Technics SU-A6 | Acurus A-250 | Radio Shack 15-band EQ | Pioneer SR-9 reverb | Cerwin Vega DX9's | Dayton 100° x 60° horns with titanium HF/MF compression drivers.
  • mufsoman
    mufsoman Posts: 632
    edited January 2014
    Going back to my question in post #13......"So I will have 2 amps, 2 subs, AVR and the rest of the gear to plug in. I was planning on having one circuit for each amp and a third for all else. Three dedicated circuits total, either 15 or 20 amps each."

    What are your alternate recommendations???


    BTW, making contact with an electrician through church so I can verify panel capacity.....I'll provide an update afterward. However, from what I have learned/read, although there's 7 slots open in the panel, the real judgement of capacity comes down to potential amp load at any given time or worse case scenario vs. max load the main breaker is rated for. For that, I need to do a little more homework on amp draw of other appliances in the house. We have natural gas, so dryer, oven, stovetop, are not electrically heated, which helps a bit.
    Parasound HCA-2003A & 2205A
    Front: Rti12's
    Center: Csi A6
    Side surrounds: Polk Rti A1's
    Atmos: Mirage Nanosats
    APC H15
    Power cords by Pepster, Morrow MA4 IC's, AQ Midnight, AQ Chocolate HDMI's[/SIZE]
    The rest is TBD.
  • amulford
    amulford Posts: 5,020
    edited January 2014
    One 15 or 20 amp circuit will fill any need you have. There is absolutely no need to run more than one.

    I would opt to run 12 Ga. Wire. If you ran a 15 A circuit, 14 would suffice. If you decided to increase to 20 A you would need to increase it to 12, so save yourself the hassle ahead of time.

    Take the time to run it isolated from other lines. I would, if possible, run it in EMT and ground the conduit at the panel. This would help shield the circuit from stray EMF noise and drain it away from the gear. So you will run 3 conductors (hot, neutral, and ground) in the conduit, and attach a ground to the conduit at the panel end of the run.
  • Glen B
    Glen B Posts: 269
    edited January 2014
    I run my 2-channel and HT system each on a single 20A circuit, and have never had a problem. The HT system circuit has running on it a 100W x 5 AVR, 200 W x 2 amp, two powered subs, EQ for the subs, two cable boxes, DVD player, and flatscreeen TV. Everything is connected through my Belkin PF-60 line conditioner, which displays current draw, which has never been more than 7 amps at normal listening levels. The HT circuit is run with 12 gauge type AC armored cable, and the 2-channel circuit is run in EMT, with individual type THHN/THWN 10 gauge wires for hot, neutral and ground.
    Main System: Denon DP-59L | Audio-Technica AT33EV | Marantz SA-11S2 | Classe DR-10 | Classe CA-300 | Classe RC-1 | PSB Stratus Gold i's | DIY Balanced AC Power Conditioner | Acoustic Zen and NeoTech cables | Oyaide and Furutech power connectors | Dedicated 20A isolated ground line.

    Home Theater: Toshiba D-VR5SU | Laptop #1 |Outlaw Audio OAW3 wireless audio system | Marantz SR-19 | Phase Linear 400 Series 2, modified | AudioSource 10.1 EQ (for subs) | Axiom M3 v3’s | Axiom VP150 | Optimus PRO-X55AVs | Dayton 12” powered subs (x2) | Belkin PureAV PF-60 line conditioner.

    Party System: Laptop #2 | Audioquest Dragonfly USB DAC | Technics SU-A6 | Acurus A-250 | Radio Shack 15-band EQ | Pioneer SR-9 reverb | Cerwin Vega DX9's | Dayton 100° x 60° horns with titanium HF/MF compression drivers.
  • Speedskater
    Speedskater Posts: 495
    edited January 2014
    Sometimes in the home theater forums you read about people several very big amps and more sub-woofers on just one 20A circuit. If you turn the amps on one at a time, you can play 'train wreck' movies way to loud on just one circuit.
  • F1nut
    F1nut Posts: 50,647
    edited January 2014
    ......"So I will have 2 amps, 2 subs, AVR and the rest of the gear to plug in. I was planning on having one circuit for each amp and a third for all else. Three dedicated circuits total, either 15 or 20 amps each."

    One 12 gauge, preferrably 10 gauge 20 amp line will be fine for that, but if you can, run all 3. Nothing better than ample clean power.
    Political Correctness'.........defined

    "A doctrine fostered by a delusional, illogical minority and rabidly promoted by an unscrupulous mainstream media, which holds forth the proposition that it is entirely possible to pick up a t-u-r-d by the clean end."


    President of Club Polk

  • rtart
    rtart Posts: 833
    edited January 2014
    IMO, you can never have too much electrical capacity to your HT. If you are running new wiring, I'd suggest 2 - 20A circuits at a minimum. I'd also run a couple 15A circuits, too. Wire is cheap to install during construction, but not so much later if you need it.

    Rarely does power needed decline as your HT 'evolves'. My main power amp is fed by two power cords, both rated at 15A minimum each. I run the amp on two dedicated 20A circuits, and have one more 20A for the other amps (I run 9.1, two monster subs and three powered speakers) and a fourth 20A circuit for the other gear like BD players, cable boxes, server, etc. I also ran a spare for expansion, if I ever need it.

    The thing to remember is that if your gear runs out of power, it won't 'tell you' by shutting down or thumping, etc. It simply won't reproduce the source material as well as it could. For example, if there is a huge explosion in a movie and your sub runs out of electrical power, the 'boom' won't be as loud as it could have been. The term is 'dynamic headroom', and some of us have paid a LOT over the years to maximize it. Modern BD sources have immense dynamic range, and sound great....if your gear has the power reserves to accurately reproduce it. If the amp runs out of power, it simply does the best it can. Kind of like a race car with a carb restrictor plate. It can do more, but is limited.

    I really don't need most of the power my HT has....most of the time. But, once in a while, the source calls for a LOT of power, and because it is available, the result is sometimes very dramatic. I've had people leave my HT during the U-571 depth charge scene, while played at reasonable sound levels. The boom is just visceral, and unexpected...and just what I intended!!
    My 7.4.4 DIY 4k Home Theater:
    Polk LSiM 707 L-C-R, LSiM702 side surrounds, LSiM 705 rears
    Polk LSiM 702s x 4 on the Ceiling Atmos speakers
    2 x SVS PB12/Plus 2's
    Denon X3700H
    Emotiva XPA11 Gen 3
    XBox One X 4k & BD and streaming
    Panasonic UB-420 4k player
    HD-A35 HD DVD
    Oppo BD-103D for hirez audio
    Technics SL-D2 TT, Grado Gold Cartridge
    JVC DLA-RS2000/NX7 projector
    Silver Ticket 120" acoustically transparent screen
    Berkline 090 electric recliners with Aura Bass Shakers
  • mufsoman
    mufsoman Posts: 632
    edited January 2014
    As rtart says above, I never understood it to be capacity as much as its headroom and separation to avoid cross interference from the various heavy users in the rig. I have been running all my gear except one sub from one 10 amp circuit without ever blowing the breaker. The separate dedicated circuits are for (mainly) separation of the amps from the rest of the system.

    With that said, I have always wondered why 20 amps? I doubt the average rig doesn't pull anywhere near that even when cranked, so why not 15 amps?
    Parasound HCA-2003A & 2205A
    Front: Rti12's
    Center: Csi A6
    Side surrounds: Polk Rti A1's
    Atmos: Mirage Nanosats
    APC H15
    Power cords by Pepster, Morrow MA4 IC's, AQ Midnight, AQ Chocolate HDMI's[/SIZE]
    The rest is TBD.
  • rpf65
    rpf65 Posts: 2,127
    edited January 2014
    You want to run a 20A capable, because you can use a 15A outlet on 20A wire. You can't use a 20A outlet on 15A wire. Better to spend the extra money up front, and not worry later. Some amps require a 20A outlet. Just change the plug yourself.