Need Help w/ Kitchen Addition Venting Range Hood

[Deleted User]
[Deleted User] Posts: 1,225
edited March 2012 in The Clubhouse
I need some help / advice with my kitchen addition. I am installing a range hood and would like to vent it to the outside. It needs to extend up the back wall 2 to 4 feet and across the ceiling about 10 to 11 feet to the outside. I am pretty sure its okay to do this as long as the fan is powerful enough. I am trying to minimize bends in the pipe and use 45 degree turns if possible. Any pointers to offer ? What size pipe do I need to use ? Suggestions welcome. Thanks. :cool:
Post edited by [Deleted User] on

Comments

  • tonyb
    tonyb Posts: 32,957
    edited March 2012
    I would imagine you'd have to check your local codes. Obviously you can't have a rinky dink hood over a 8 burner Wolf stove. As far as that length to get to the outside, I see condensation as a possible problem and grease build up. Cant go straight up ?
    HT SYSTEM-
    Sony 850c 4k
    Pioneer elite vhx 21
    Sony 4k BRP
    SVS SB-2000
    Polk Sig. 20's
    Polk FX500 surrounds

    Cables-
    Acoustic zen Satori speaker cables
    Acoustic zen Matrix 2 IC's
    Wireworld eclipse 7 ic's
    Audio metallurgy ga-o digital cable

    Kitchen

    Sonos zp90
    Grant Fidelity tube dac
    B&k 1420
    lsi 9's
  • WagnerRC
    WagnerRC Posts: 2,155
    edited March 2012
    mount a fan close to the exit for better extraction
  • dkg999
    dkg999 Posts: 5,647
    edited March 2012
    That's a long run with moisture laden air cooling on the way to the exit. I don't remember what code says and don't have any of my reference books available at the moment. Can you downdraft to the basement and a more accessible duct run? Can you go up through the roof and a shorter run? +1 on having the fan unit closer to the exit.
    DKG999
    HT System: LSi9, LSiCx2, LSiFX, LSi7, SVS 20-39 PC+, B&K 507.s2 AVR, B&K Ref 125.2, Tripplite LCR-2400, Cambridge 650BD, Signal Cable PC/SC, BJC IC, Samsung 55" LED

    Music System: Magnepan 1.6QR, SVS SB12+, ARC pre, Parasound HCA1500 vertically bi-amped, Jolida CDP, Pro-Ject RM5.1SE TT, Pro-Ject TubeBox SE phono pre, SBT, PS Audio DLIII DAC
  • cristo
    cristo Posts: 231
    edited March 2012
    +1 on avoiding rinky dink hoods, like the kind you usually see at lowes, home depot, etc.
    We got a Five Star rangetop (4 burners with a central griddle) and the Five Star hood that
    matched to it flows great, if a little noisy, even with about 10 feet of pipe to the exit..
    cristo

    NAD C 545BEE cd player, Philips AF877 turntable / Shure V15V-MR with JICO SAS stylus,
    Tascam 122 mkIII cassette deck, Harman Kardon 3480 receiver, Terk FM-50 antenna in the attic,
    Soundcraftsmen SE550 stereo equalizer, Polk Monitor 10a speakers
    (with Sonicraft/Solen/Mills crossover rebuild)
  • SCompRacer
    SCompRacer Posts: 8,494
    edited March 2012
    Maybe consider a critter guard over the exterior vent. Like this.

    51%2BinXkD-YL._SL500_AA300_.jpg

    Shortly after we moved in our house, we had a Grackle that hung off the siding and opened the flap door and crawled in the vent pipe looking for a new home. After evicting it I installed a guard.
    Salk SoundScape 8's * Audio Research Reference 3 * Bottlehead Eros Phono * Park's Audio Budgie SUT * Krell KSA-250 * Harmonic Technology Pro 9+ * Signature Series Sonore Music Server w/Deux PS * Roon * Gustard R26 DAC / Singxer SU-6 DDC * Heavy Plinth Lenco L75 Idler Drive * AA MG-1 Linear Air Bearing Arm * AT33PTG/II & Denon 103R * Richard Gray 600S * NHT B-12d subs * GIK Acoustic Treatments * Sennheiser HD650 *
  • Joe08867
    Joe08867 Posts: 3,919
    edited March 2012
    critter guards are a real good idea.
  • mrbiron
    mrbiron Posts: 5,711
    edited March 2012
    Check the unit cut sheet on this. It will tell you the maximum run and will step it back with every 90 degree bend that you put in the run.
    The top will most likely have a knock-out for a rectangular and/or ~6" duct or at least that is roughly the size for the 200+ that we just put in the project my company is doing. Your run i relatively short and you won't have a problem with properly venting this. Our max run is in the 30' range so do not fret about that. Again, your unit cut sheet will cover this.
    Where’s the KABOOM?!?! There’s supposed to be an Earth shattering KABOOM!!!
  • [Deleted User]
    [Deleted User] Posts: 1,225
    edited March 2012
    mrbiron wrote: »
    Check the unit cut sheet on this. It will tell you the maximum run and will step it back with every 90 degree bend that you put in the run.
    The top will most likely have a knock-out for a rectangular and/or ~6" duct or at least that is roughly the size for the 200+ that we just put in the project my company is doing. Your run i relatively short and you won't have a problem with properly venting this. Our max run is in the 30' range so do not fret about that. Again, your unit cut sheet will cover this.

    Sounds like you do a lot of this sort of thing. Any recommendation on brands to use or to avoid ? :cool:
  • michael1947
    michael1947 Posts: 775
    edited March 2012
    Can you go down...into the basement or crawl space. This would eliminate unsightly business in the kitchen or at least cut cost way down as you could use inexpensive pipe. Also, can you skin the outer surface, drywall, plaster, wood from the wall behind the stove and go up within the wall with shallow rectangular pipe like a 3 x 12.
    Main Family Room: Sony 46 LCD, Sony Blue Ray, Sony DVD/VCR combo,Onkyo TXNR 708, Parasound 5250,
    Polk SDS-SRS with mods, CSI 5 center + Klipsch SC2, Polk RT2000P rears, Klipsch KG 1.5's sides, Polk Micro Pro 1000, Polk Micro Pro 2000, Polk SW505, Belkin PF60, Signal Cable Classics,Monster IC's, 2 15 amp circuits & 1 20 amp circuit.

    Living Room: Belkin PF60, Parasound HCA2200, MIT ProlineEXP balanced IC's,Emotiva XDA-1 DAC/Pre,Emotiva ERC2 transport,MIT AVT2, Polk LSI 9's.
  • mrbiron
    mrbiron Posts: 5,711
    edited March 2012
    Sounds like you do a lot of this sort of thing. Any recommendation on brands to use or to avoid ?

    I work for a large scale residential development (apartment complexes) general contractor and we have corporate accounts with GE and Whirlpool buying appliances by the thousands for our clients per year. When it comes to hood vents, there really isn't much to worry about as the failure rate is in the ballpark of 1 in 50 that has a shot motor/loud fan. It's the other, more complicated appliances that you need to shop around for.

    Happy Shopping :cheesygrin:
    Where’s the KABOOM?!?! There’s supposed to be an Earth shattering KABOOM!!!
  • [Deleted User]
    [Deleted User] Posts: 1,225
    edited March 2012
    Can you go down...into the basement or crawl space.

    That part of the house is over a crawlspace and I would prefer not to go down. I will be installing a freestanding range and I don't think you can downvent those. One of the options I have stumbled across is by a company called Vent-A-Hood and it looks like they have some interesting innovations for vent / no vent as well as some proprietary technologies. I will be seriously checking into them. Cheers. :cool:
  • drselect
    drselect Posts: 664
    edited March 2012
    nap wrote: »
    One of the options I have stumbled across is by a company called Vent-A-Hood and it looks like they have some interesting innovations for vent / no vent as well as some proprietary technologies. I will be seriously checking into them. Cheers. :cool:
    nap, we have a Vent-A-hood. I think I have posted picture of it some place on here before. It is well constructed and have never had any problems with it. Its a beast thought. Had to have a special 12" duct and roof vent made for it. Helps to have a big utility sink to clean the fans on it. Last summer I just took them outside and cleaned them with a powerwasher.
  • muncybob
    muncybob Posts: 3,039
    edited March 2012
    Good timing on this thread as the Mrs wants me to install one. The Vent-A-Hoods look real nice, hope we can find a dealer that we can go look at them.
    The exhaust piping for us would exit directly from the rear and have to travel thru an unheated air space of apprx. 10'. I wonder if I'll have condensation issues?
    Yep, my name really is Bob.
    Parasound HCA1500A(indoor sound) and HCA1000(outdoor sound), Dynaco PAS4, Denon DP1200 w/Shure V15 Type V and Jico SAS stylus, Marantz UD7007, Polk L600, Rythmik L12 sub.
  • disneyjoe7
    disneyjoe7 Posts: 11,435
    edited March 2012
    Not sure this would help you, but have a down draft vent in my house which is under the concrete slab. Its ran in pvc under floor, I recently seen this pipe and didn't see any condensation problems. The house is 15 yrs old, so thinking if a problem, I would of seen it.

    Speakers
    Carver Amazing Fronts
    CS400i Center
    RT800i's Rears
    Sub Paradigm Servo 15

    Electronics
    Conrad Johnson PV-5 pre-amp
    Parasound Halo A23
    Pioneer 84TXSi AVR
    Pioneer 79Avi DVD
    Sony CX400 CD changer
    Panasonic 42-PX60U Plasma
    WMC Win7 32bit HD DVR


  • [Deleted User]
    [Deleted User] Posts: 1,225
    edited March 2012
    muncybob wrote: »
    Good timing on this thread as the Mrs wants me to install one. The Vent-A-Hoods look real nice, hope we can find a dealer that we can go look at them.
    The exhaust piping for us would exit directly from the rear and have to travel thru an unheated air space of apprx. 10'. I wonder if I'll have condensation issues?

    I believe you are okay provided you have enough cfm and the proper size vent pipe. Some of the hoods I have looked at require 8 inch pipe. Also, minimize bends and use 45 degree turns instead of 90. HTH. Cheers. :cool:
  • muncybob
    muncybob Posts: 3,039
    edited March 2012
    nap, some of the Broans I've looked at on the net have higher rated cfm and lower sone than the Vent-A-Hoods and I believe a lower cost. Other than some of the accessories you can get with the Vent-A's I'm having a hard time justifying the additional expense. What am I missing here?
    Yep, my name really is Bob.
    Parasound HCA1500A(indoor sound) and HCA1000(outdoor sound), Dynaco PAS4, Denon DP1200 w/Shure V15 Type V and Jico SAS stylus, Marantz UD7007, Polk L600, Rythmik L12 sub.
  • jimmydep
    jimmydep Posts: 1,305
    edited March 2012
    As a long time contractor and building inspector in NJ., I have installed and inspected hundreds of exhaust hoods. Before installing any pipe check the manufacture for the minimum size and maximum legnth allowed. I have never seen a hood that used less than a 6" round pipe. The pipe should be 26ga steel and should have a smooth interior with taped joints, and a metal vent hood outside, don't use flex aluminum pipe as it doesn't meet most codes and grease will collect inside. If space doesn't allow for a round pipe you could use a 3.5x10" rectangular pipe. Note that any exhaust piping running through unheated spaces should be insulated with R-8 insulation.